1. What are the advantages and disadvantages of both design?
2. Is cascading of UPS advisable or applicable?
1. What are the advantages and disadvantages of both design?
2. Is cascading of UPS advisable or applicable?
#1: I believe maintenance cost and manageability is the biggest benefit of centralized UPSes.
One big battery bank is easier to maintain, service, and secure than many smaller units spread out over a wide area.
Ease of scalability may also play a role. Every time you add a camera or switch, a distributed system could prove expensive to grow.
On the flip side, a distributed system may make it easier to manage loads. If one subsystem needs more power, you just locally add bigger/more batteries.
For your #2: Do you mean use both distributed and centralized UPSes at the same time?
Yes. hybrid, since 24/7 surveillance is a requirement.
I think the problem with distributed ups system is that when the ups is not connected to an emergency power line,while on centralized , a short ciircuit on any line will affect the whole system. am i right?
In addition to Brian's excellent points I would add a couple others.
Central UPS Benefits:
Distributed UPS Benefits:
By cascading do you mean for redundancy when two similar units are put in series with a 'make then break' bypass switch, i.e, as opposed to a parallel load sharing configuration?
A centralized ups connected to all distributed ups. Is this possible?
It's possible but in my experience, (for data centers at least), it's not the normal way that redundancy is implemented for HA systems. Redundancy is usually achieved by the pairing of two identical units in either a serial cascade or a parallel load sharing scenario.
You could try and cascade several smaller distributed ones into one large one but sizing it properly may be difficult.
Also, it will be extremely hard to estimate your autonomy/endurance as different UPSes engage and disengage from the central UPS. Therefore creating an acceptable SLA may be challenging.
Also, short circuit protection can be implemented by using multiple downstream PDU's.
Can you divulge a little more about the application in terms of load size, load type, topology and emergency power generation?
How many 9's are required for uptime?
Thanks.
five 9's. 20 Distribution Switch (24 port PoE Switch) , 2 Fiber Switch (24 port), 10 PTZ camera, 140 fixed camera, in a 10 storey building
The servers/NVRs and Fiber switches are all together in one room?
How many? Dual corded with dual power supplies?
Dedicated mains circuits to each floor/zone from a central location (server room)?
Diesel generators? 24/7 on-site staff to perform emergency power failover?
Servers /NVRs and Fiber Swicthes are all in the Control Room.
7 NVR/servers
There is a main circuit breaker in the control room for each floor level.
Diesel Generator. There is an on-site staff to perform emergency power fail over.