Recommendations For Commercial Grade CO Detectors With Genetec?
Has anyone installed carbon monoxide detectors connected to VMS for alerts and reporting? I am looking for this product with integration to Genetec if exists.
Thanks
I believe this type of integration usually is done via an intrusion panel integration with Genetec. They support Bosch, Honeywell Galaxy and several other panel brands.
When you say "alerts and reporting" this implies Life safety functions and standards compliance.
If this is the case you would likely need a Listed Fire Alarm Control Panel to monitor the device and provide you output(s) to the VMS.
Your title might be a little misleading. When that’s all I read I thought you were talking about residential use. After seeing Genetec, that changed the message. Are you thinking about these type systems?
I don’t work for them but have designed these type products into below ground parking structures for methane and other gas detection.
Thank you for replying. Sorry about the misleading subject line.
I updated the subject title, but let me know if I should change it further.