Table 300.5 in the 2011 NEC calls for depths up to 24" depending on the installation and conduit used. This is for 0-600V. PoE is typically 48 V with some devices using 24V, 18V, 50+? I do not see any exception for network cable?
830.47 covers Network Powered Broadband Communications systems and has specific depth requirements as well.
Either way, if not covered in concrete or driveway, it usually needs to go down 12" to 24"
Can anyone cite where POE cables are exempt?
Granted, I doubt anyone is at any risk over a POE cable.
But we use this to justify our trenching expense. We tell customers we have to bury so deep so that we are not asked to kick a little dirt over it. I have seen many failures due to this. One company I know buried a line 3 times because it kept getting cut. And it still got cut cut.