Hi

 

What is the maximum amperage one can pass safely ( meaning no cable overheating ) on a 200 feet Cat 5e span? Not necessarily PoE (not excluding the use of a.High Power PoE Injector /Splitter pair either) which seems to allow up to 60 watts on 2 pairs ... We would like to use the Cable as a regular DC transport cable . We need 100 watts @ 48 Volts about 2.5 amps ... We don't plan to use RJ45 if the cable is used as a regular DC cable carrying Positive and Negative on two pairs each ....

Thanks in advance

Avatar
Brian Rhodes
Jul 11, 2018
IPVMU Certified

IEEE 802.3af/at/bt/ac often discusses amperage/power limits as a function of heat dissapation through cable jackets. The power limits are capped out of concern a bundle of PoE cable ignites, so the wattage limits correspond to conductor size and number of 4-pair cables per bundle.  For example, bt/ac mandates use of Cat6, and so on.

So your question:

We would like to use the Cable as a regular DC transport cable . We need 100 watts @ 48 Volts about 2.5 amps 

If this is a single cable, it can likely handle it just fine. But if you're bundling multiple cables together, the answer changes.  See this chart (table 725.144 in the bt standard)

Also, can you run a larger conduction (bigger wire) Cat6 rather than Cat5?

(1)
U
Undisclosed #2
Jul 11, 2018
IPVMU Certified

If this is a single cable, it can likely handle it just fine. But if you're bundling multiple cables together, the answer changes. 

The way I am reading the chart, at 22-23AWG (the red arrow), according to the chart, the answer is always > 2.5A.  

And even at 24AWG, the worst case (192 60C cables) is 2.4A. 

Am I reading it correctly?

U
Undisclosed #2
Jul 11, 2018
IPVMU Certified

We need 100 watts @ 48 Volts about 2.5 amps...

Btw, in a DC circuit, 2.5A @ 48V = 120W

(1)
(1)
U
Undisclosed #3
Jul 11, 2018

To maintain 802.3bt Type 4, you must be terminating between a compliant PSE and PD. 

What is the device that needs power? Is it PoE? Or are you trying cannibalize the cat5 wire? If so you have to make sure your 2.5amp covers any peak voltage needed by your device.

Avoid the fire hazard and run the appropriate cable!

(1)
UI
Undisclosed Integrator #4
Jul 11, 2018

Avoid the fire hazard and run the appropriate cable!

Please this.  As an End User even if it is going to cost extra or take more time please don't just wing it or go by internet wisdom.  Be up front with me run the appropriate cable and bill me accordingly.  Much better for my business/home and your business to just do it right.  

(2)
UI
Undisclosed Integrator #5
Jul 11, 2018

Well, it’s been awhile since I dove into the code books but as I recall, you should consider each conductor that is separated to be its own conductor. 

Guys will double, triple, quadruple up pairs on cables to increase amperage capacity.  It makes sense, until a single or couple of solid conductors break somewhere in the line.

Then, you have one or two small gauge wires carrying the load.  When you overload a conductor....guess what happens?  It generates heat/fire.

I’m sure PoE devices take this into account when single conductors or pairs become disabled, but just twisting them together does not make a “stranded” cable. 

Just my 2 Watts worth. 

(1)
U
Undisclosed #3
Jul 12, 2018

True Story

(2)
(4)
UI
Undisclosed Integrator #1
Jul 13, 2018

Hi

Reading the news and technical information from afar, one hears talks about PoE standards for up to 100 watts,  the so-call PoE++ ..etc. The reality is that at those levels of power heat generation in a cable becomes substantial . Cat 5e predates PoE802.3 at for example let alone going full tilt at 100 watts... 

I will back off and pull a pair of 14 AWG cable ... Made for the purpose of power transmission that will easily carry up to 10 A .. Better to err on the safe side when risks of destruction are considerable.. Pulling those copper wires will be as painful as the proverbial toot ... but is is worth the pain and inconvenience.

Thanks all. Case closed!

:) 

(1)
UI
Undisclosed Integrator #5
Jul 13, 2018

Just make sure you do a voltage drop calculation.  #14awg is huge for low voltage guys and tiny for electricians.  It’s all perspective.

I knew a guy who ran #18awg to be safe on a project and didn’t know why things didn’t work right.  I did a quick VD for him and most runs needed to be #10agw.

Spool up some #2awg some time for fun. 