We ran into a job that involved a new access control system consisting of Maglocks on the main front entry doors. Per the code requirements we installed the required egress motion sensor, egress pushbutton (marked with "push to exit) with a 30 second pneumatic feature. We connected the pneumatic button in series with the lock power at the door and also connected one side of the DPDT relay in the REX motion in series with the lock power at the door so that the Maglock would unlock without requiring the logic of the access control panel. This configuration also met the requirement that if the REX motion lost power the Maglock would unlock. We used an Altronix AL600ULACM power supply with an ACM8 fire release relay board to allow connection from the existing addressable fire alarm system. The fire alarm contractor provided us with an addressable relay at our access panel and it was configured and tested to change state upon any general fire alarm. This relay was connected to our power supply per the manufacturers instructions and the connection provided proper supervision from the addressable relay to our power supply fire alarm input.
The local AHJ had a problem with the fire alarm systems logic to always function correctly. His concern was that the because the fire alarm relay was addressable, it might not function as intended if the fire alarm panel had logic problems. He wanted a dry contact output directly from the fire panel to be tied in series with the Maglock power source. We discussed the fact that the entire addressable fire alarm system including all addressable inputs (pull stations, smoke detectors, and other addressable devices also relied on the same fire alarm panel logic to be operational as well. He did not see it that way and was stuck on this fire alarm relay issue. We ended up doing it his way.
When it came time to test the system for proper release upon a power failure, he wanted to shut down power to the entire plant at the main service panel to ensure that we were actually simulating a power outage event rather than just removing power from our control equipment. This was a large plant with many employees. This is when the plant director stepped in and made a few phone calls downtown. The end result was that the plant power was not shut down, and he agreed to let us simulate a power outage by removing power from our control equipment to verify the Maglocks did in fact unlock.