Cameras Mounted On Poles Primer

JH
John Honovich
Aug 15, 2016
IPVM
Poles are a popular but challenging choice for deploying surveillance cameras. Poles are indispensable for putting cameras at the right height to get the best picture and for keeping cameras out of ha...

Read the full report here
UI
Undisclosed Integrator #1
Aug 15, 2016

Ive had good experience with a company called Strong Poles based in Texas. they sell an adapter that you set in a tube of concrete that goes a few feet into the ground. once dry you attach the pole to that anchor.

very stable and does not shake with the wind

(2)
(2)
AZ
Adel ZAHRAN
Aug 15, 2016

it is great subject, i had already working on similar project for government sector in Saudi

(1)
Avatar
Craig Mc Cluskey
Aug 17, 2016

Good article. The photograph,

,

however, shows the grounding conductor installed with an inductor wound in it. This will increase the impedance between the ground rod and the item which is grounded. This will be particularly noticeable with current waveforms with fast risetimes, like in a lightning strike, which is exactly when you want a good, low impedance ground.

(2)
(1)
(3)
RD
Rob Dunham
Jan 16, 2018
Tailored IT Solutions

Code in many areas requires it to be a bare (non-insulated), solid copper conductor.

RP
Robert Peters
Oct 30, 2020
IPVMU Certified

I would be more concerned with the coil which while practical for some movement / installation relief, does form an inductor. However small of a reactance, its still unwanted when you really need a low impedance path for current from a lightning discharge.

Avatar
Joseph Marotta
Sep 07, 2016
IPVMU Certified

Craig Mc Cluskey beat me to the coiled ground conductor shown in the picture! Craig's comment was excellent.

Concerning depth of the ground rod, in the US, the National Electrical Code book section 250.53(G) requires a ground rod installed such that at least 8 feet of length is in contact with the soil, and driven to a depth of not less than 8 feet. Also, the upper end of the rod shall be flush with or below ground level (for protection) unless the above-ground end and conductor attachment are protected from physical damage (such as enclosed in metal, wood, or equivalent protective covering per section 250.10).

Outside the US, it's probably best if the installer check with the local authority having jurisdiction for specific grounding requirements.

The article was a good primer to pole mounted cameras, thanks Brian!

In a follow up article, it would be very helpful if you could include photos of actual camera installs on round metal poles, timber poles, and even on metal poles with light fixtures attached.

(3)
Avatar
Craig Mc Cluskey
Sep 08, 2016

Thank you, Joseph, for your compliment.

Yes, photographs of actual camera installs would be quite helpful.

(1)
U
Undisclosed #2
Sep 08, 2016
IPVMU Certified

Its ok, all their device cables look like this to balance it out:

Related: Tie Knots In Low-Voltage Cable

(1)
(2)
Avatar
Brian Rhodes
Sep 09, 2016
IPVMU Certified

In a follow up article, it would be very helpful if you could include photos of actual camera installs on round metal poles, timber poles, and even on metal poles with light fixtures attached.

Thanks for the suggestion. It's now the the queue!

(1)